Re: fan aerolic power calculation
iIF U PUT Pa = 1mmwg/9.81 in Watt = Pa * m3/s than Watt = mmwg*m3/s divided by 9.81 Than kiloWatt = mmwg * m3/s /( 1000*9.81) pl. comment
Know the answer to this question? Join the community and register for a free guest account to post a reply.
79 posts
Re: fan aerolic power calculation
Mr xxxx
since you are taking the reading in mmwg ,you have to multiply 9.81 to convert it to Pa then divide it by 1000 to get Kw. you are doing in a reverse way.
The Kw calculation is nothing but work done per second
and work done is always the air handled and pressure
rectify dear
chari
239 posts
Re: fan aerolic power calculation
no i am not doing the reverse way. just see 1 mmwg = 9.81 Pa than Pa = 1mmwg / 9.81 than put the value of Pa in the formula = Pa * volume (m3/s) it becomes watt = (mmwg/9.81) * volume (m3/s) so u do not get 102 in denomenator pl. check
79 posts
Re: fan aerolic power calculation
Let us take an example of a fan
Pressure = 5393 Pa, Volume =21.1m3/sec KWatt = 5393*21.1/1000 = 113.7 Kw
Now converting pascal to mmwg by deviding 9.81
pressure = 550mmwg , Volume =21.1m3/sec KWatt = 550*21.1/102= 113.7 Kw
1mmwg = 9.81Pa
Then 2mmwg = 19.62 Pa
X mmwg = X * 9.81 Pa, it will be a multiplication not devidation, i Think you are clear from the data